Huanyang Vfd Wiring & Setup (vfd Newbie)

Discussion in 'ELECTRICAL ISSUES - POWER YOUR MACHINES & SHOP' started by jbolt, Mar 29, 2015.

  1. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Hi All, I'm to the point on my mill belt drive conversion that it is time to setup the VFD / Motor. This is my first VFD so I need some guidance getting it setup properly. The Huanyang VFD and Hallmark motor were free to me so I will be using these for the first go. If I am not satisfied with the performance I will upgrade to better equipment later.

    Here are the VFD and motor labels.
    vfdvlabel.gif motor label.gif

    First I want to verify I have the base wiring done correctly. The VFD is 220v so I have the motor wired in the "Low Volt" configuration.

    Three wires from the motor "U/L1", "V/L2", "W/L3" go to the corresponding "U", "V", "W" terminals on the VDF.

    Motor ground from the motor case ground screw to the ground terminal in the VDF (lug to the right of terminal "W")

    Motor shield wire unattached at the motor end and terminated at the VFD chasis ground.

    Main 220 power is L1 and L2 from a contactor to terminals "R", and "S" on the VFD.

    Main ground wire to the VFD chasis terminal.

    I have not powered it up yet.

    vfd wiring01.gif

    If the base wiring looks good then what is the next step in configuring the VFD?

    The VFD will be controlled from Mach3 through a PMDX126 BOB, Eithernet Smooth Stepper and PMDX-107 motor control card.

    I'm thinking it would be best to get the VFD/motor running off the key pad before doing the Mach3 setup???

    Jay
     
  2. mksj

    mksj Active User H-M Supporter-Premium

    Likes Received:
    1,276
    Trophy Points:
    113
    City:
    Tucson
    State:
    Arizona

    -Return to Top-

    The way you have wired it looks correct. You should have the incoming single phase power fused or going to a breaker before start-up. You should do basic programming before running the motor, i.e. enter the motor parameters (PD141-144) into the VFD. Base frequency should be 60Hz (PD176). Agree, make sure everything is working manually before external controls are added. If you require very quick brake times, you might need to add a braking resistor, but less of an issue on a mill vs. lathe.
     
    JimDawson likes this.
  3. awander

    awander United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Upper Black Eddy

    -Return to Top-

    Make sure your motor is wired per the "low voltage" diagram.
     
  4. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Thanks guys, I do have circuit breakers before the contactor and the motor is wired for Low Volt.

    Once I actually started pushing buttons it's pretty straight forward (if you understand what the parameters do). The Commissioning part of the manual is terrible for understanding what buttons to push.

    Okay here is what I programmed.

    pd001 = 0, run command = operator (manual)
    pd003 = 60.00, main frequency
    pdoo4 = 60.00, base frequency
    pd005 = 120.00, max frequency
    pd008 = 220, max voltage
    pd141 = 220, rated motor voltage
    pd142 = 8.0, rated motor current
    pd143 = 4, motor pole number
    pd144 = 1725, rated motor revolution
    pd176 = 60.00, inverter frequency standard

    Motor started and ran fine with no load, I ran it no load for 30 min . I then hooked up the belt to the the 1:2 ratio pulleys and ran the spindle for 30min at 60hz. And last I swapped to the 2:1 ratio pulleys and ran it at 60hz and then 120hz for 15 min each. The outside of the motor case stayed a constant 108 deg which I think is reasonable.

    So far I think I have the base programming correct. Please let me know if anything above looks wrong?

    I do have some noise/vibration coming from the splinded shaft area of the spindle which I think is the somewhat loose fit of the splined drive sleeve to splined spindle shaft connection but that problem is for a different thread...

    Next step is getting Mach3 setup??? More reading to do.........

    Jay
     
    JimDawson likes this.
  5. stupoty

    stupoty Active User Active Member

    Likes Received:
    207
    Trophy Points:
    63
    City:
    London

    -Return to Top-

    I have two of the hy brand invertors, one has earth continuity on the two lower screws marked with earth symbol, the other one dosn't. Definetly worth a check.

    Stuart
     
  6. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Thanks Stuart I will check!

    Jay
     
  7. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    I need to verify the wiring from the motor controller (PMD-107) to the VFD.

    This is what I have come up with.

    PMDX-107 ---> VFD
    Pin 6 - Rev/Dir REV (reverse run)
    Pin 5 - Fwd/Run FOR (forward run)
    Pin 4 - COM (common terminal for relays, pins 5 & 6) DCM (common terminal of digital and control signals)
    Pin 3 - Aref (not used)
    Pin 2 - Aout (spindle speed anolaog control voltage) VI (analog voltage frequency reference input)
    Pin 1 - Agnd (VSD ground reference) ACM (common termnal of analog and

    PMDX Config settings (dip switches)
    Config 1 = Off (Normal Mode)
    Config 2 = Off (Normal Mode)
    Config 3 = Off (relays operate as for and reverse control signals)
    Config 4 = Off (charge pump signal required)
    Slow = Off (fast PWM filter response)
    5v/10v = Off (10v reference)
     
  8. mksj

    mksj Active User H-M Supporter-Premium

    Likes Received:
    1,276
    Trophy Points:
    113
    City:
    Tucson
    State:
    Arizona

    -Return to Top-

    Just a note on the motor settings, probably would use PD005 of 90 or 100Hz, unless you have some information that indicates a higher top speed. 120Hz may be OK for short periods of time, but not sure I would run this particular motor for long periods.
     
  9. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    It was my understanding that these motors would tolerate up to about twice their rated hz? Maybe I am mistaken or that is for a higher quality motor?

    I was planning on limiting the spindle to 6k which works out to around 105hz. Would that be okay?
     
  10. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    I just realized the formatting got screwed up on post #7

    Try again,

    I need to verify the wiring from the motor controller (PMD-107) to the VFD.

    This is what I have come up with.

    PMDX-107 ---> VFD
    Pin 6 - Rev/Dir ----> REV (reverse run)
    Pin 5 - Fwd/Run ----> FOR (forward run)
    Pin 4 - COM (common terminal for relays, pins 5 & 6) ----> DCM (common terminal of digital and control signals)
    Pin 3 - Aref (not used)
    Pin 2 - Aout (spindle speed analog control voltage) ----> VI (analog voltage frequency reference input)
    Pin 1 - Agnd (VSD ground reference) ----> ACM (common terminal of analog and control signals)

    PMDX Config settings (dip switches)
    Config 1 = Off (Normal Mode)
    Config 2 = Off (Normal Mode)
    Config 3 = Off (relays operate as for and reverse control signals)
    Config 4 = Off (charge pump signal required)
    Slow = Off (fast PWM filter response) (may need to be changed to slow if VFD cannot keep up)
    5v/10v = Off (10v reference)
     
  11. mksj

    mksj Active User H-M Supporter-Premium

    Likes Received:
    1,276
    Trophy Points:
    113
    City:
    Tucson
    State:
    Arizona

    -Return to Top-

    It is my understanding that the bearings are the same, so it is not necessarily a mechanical limitation. There may be some limitations as to developing full horsepower out to 2X rated speed and torque can fall off in a somewhat more non-linear manner above 1.5X base speed. A lot depends on the motor specs, so motors like the Marathon BlueMax and BLackMax 3 phase 1750 RPM motors are rated up to 5-6K. Most of the better built 3 phase motors are OK up to 2X base speed. Just wouldn't push the motor hard for long periods at the higher RPM.
     
  12. countryguy

    countryguy United States Active User Active Member

    Likes Received:
    185
    Trophy Points:
    43
    Location:
    Fenton, MI
    City:
    Fenton
    State:
    Michigan

    -Return to Top-

    If I recall, there are true Inverter rated motors w/ special insulated armature windings and current capabilities. There were also issues w/ the heat dissipation on non-VFD rated motes. On these better VFD Motors, a higher temp capability is then allowed based on higher currents when pushing Hz up. I'm sure the Bearings have some manner of heat rating as well so thats possibly a factor. Non-Inverter rated motors and older motors can melt down and burn up. I posted a link to some images in the past. I think when we say up to 2x for short times, we are simply exercising the older motors saftey margins for sake of speed. That's what I recall on a really Sunny 55' day here in MI.

    CG.


     
  13. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Steve Stallings at PMDX confirmed my control wiring and I can now turn the spindle on/off with Mach3. My only problem at this point is I cannot get the spindle speed to change with "S" commands. It always goes to 100%. I can slow and speedup the spindle with the override.

    Jay
     
  14. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Thanjs for all the feedback so far. I am still looking for a solution as to why I cannot control the spindle speed with "S" commands in Mach3.

    These are my settings.

    PMDX-126 BOB, PMDX-107 Motor Control, ESS Motion Controller.

    MOTOR, 220v, 2hp, 3ph, 1725rpm, inverter duty, class F

    VFD = Huanyang HY02D223B Settings

    pd001 = 1, run command = external terminals
    PD002 = 1, operating frequency source = external terminals
    pd003 = 60.00, main frequency
    pdoo4 = 60.00, base frequency
    pd005 = 120.00, max frequency
    pd008 = 220, max voltage
    pd141 = 220, rated motor voltage
    pd142 = 8.0, rated motor current
    pd143 = 4, motor pole number
    pd144 = 1725, rated motor revolution
    pd176 = 60.00, inverter frequency standard


    ESS Settings

    SPINDLE
    PWM, base hz 25


    Mach3 Settings

    RELAY CONTROL, disabled

    MOTOR CONTROL
    Use Spindle Motor Output
    PWM Control
    PWM Base Freq = 25
    Minimum PWM 5%

    SPINDLE MOTOR TUNING
    Steps per = 1000
    Velocity = 60
    Acceleration = 5000

    PULLEY SELECTION
    Pulley 1, Min Speed = 300, Max Speed = 6000, Ratio = 2 (4" motor pulley, 2" spindle pulley)
    Pulley 2, Min Speed = 75, Max Speed = 1500, Ratio = 0.5 (2" motor pulley, 4" spindle pulley)

    Thanks
    Jay
     
  15. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    I finally figured out the final piece of the puzzle. PD072 was factory set to 400hz and was screwing up the scaling. I reset this to 105hz and reran the built-in calibration on the PMDX-107 motor control card. I was able to tune the max spindle speed to 6000 rpm and now the scaling in Mach3 works perfectly.

    Jay
     
  16. cathead

    cathead Active User Active Member

    Likes Received:
    618
    Trophy Points:
    93
    City:
    Bemidji
    State:
    Minnesota

    -Return to Top-

    Greetings,

    I just purchased a HuanYang GT series inverter (7.5KW) and the instructions are unclear to me. RSandT are the inputs but no where in this manual can I find
    a reference to which input wires go where for 220 volt single phase operation. I think R and S are the 220 inputs but don't know where to hook up the neutral wire, my guess is to ground and not
    the T terminal. The manual is lacking in my opinion. I'm hoping someone knows.

    Thanks.
     
    Last edited: Dec 10, 2015
  17. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    On my 2.2kw unit it is a 3 wire hookup for single phase Line 1 and Line 2 of the 220 go to R & S and Ground to the Ground terminal. T is for a 3-phase input and not used. Neutral is not used for the VFD.

    Jay
     
    cathead likes this.
  18. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,767
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    Do Not connect the neutral to the VFD. It would be a direct short!:chemist:

    The 7.5KW VFD is not really designed for single phase input, but according to the manual you can connect to any 2 of the R, S, T terminals for single phase operation.
    .
    .
     
    cathead likes this.
  19. cathead

    cathead Active User Active Member

    Likes Received:
    618
    Trophy Points:
    93
    City:
    Bemidji
    State:
    Minnesota

    -Return to Top-

    Jim,

    Thanks for responding. I was hoping to hear from you. Do I leave the neutral unconnected or can the neutral be applied to the ground lug?






     
    JimDawson likes this.
  20. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,767
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    Just leave the neutral unconnected, it is not used in this circuit. But do connect the ground to the ground terminal.
     
    cathead likes this.
  21. cathead

    cathead Active User Active Member

    Likes Received:
    618
    Trophy Points:
    93
    City:
    Bemidji
    State:
    Minnesota

    -Return to Top-

    OK, I understand now. Your knowledge and assistance is much appreciated.
    I can't thank you enough! Burt




     
    JimDawson likes this.
  22. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,767
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    Thank you for the kind words. It's my pleasure to help out where I can.
     
    cathead likes this.
  23. stupoty

    stupoty Active User Active Member

    Likes Received:
    207
    Trophy Points:
    63
    City:
    London

    -Return to Top-

    How do us 220v circuits work ? are they phase + phase ? (2 x 110v out of phase ?) as

    Maybe we should have a sticky or something some ware, Just realized that us 220v is phase and phase where as European 220v is single phase, i.e. live and neutral go into the VFD input hear.

    Stuart
     
  24. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,767
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    Our neutral is derived from a grounded center tap on the transformer. I should note that I looked at the OP's location before I made my recommendations. If he would have been in Europe or GB, my answer would have been different.

    L14-3.gif images?q=tbn:ANd9GcQ5dKXa4HQwj84xyW3J6dFYjBpEepijRm9hoylvEHrCwxXsMqSH.jpg
     
    Last edited: Dec 11, 2015
  25. mksj

    mksj Active User H-M Supporter-Premium

    Likes Received:
    1,276
    Trophy Points:
    113
    City:
    Tucson
    State:
    Arizona

    -Return to Top-

    Nice chart on the wiring and differences. I believe the terminology is the US 240V is split phase, EU would be single phase 240V. VFDs used in the US that are 220-240V single phase are hot to hot, there are also 120V in that are hot and neutral and they output 3 phase 200-240V. Neutral should not be tied to ground except at the main electrical box.
    Electrical US vs. EU.PNG
     
    Fitter Bill, cathead, sanddan and 2 others like this.
  26. sanddan

    sanddan Active User H-M Supporter-Premium

    Likes Received:
    606
    Trophy Points:
    93
    City:
    Damascus
    State:
    Oregon

    -Return to Top-

    Thanks guys for the electrical class, great info to bookmark.
     
  27. dooshare

    dooshare Canada Iron Registered Member

    Likes Received:
    1
    Trophy Points:
    3
    City:
    sherbrooke
    State:
    Province du Quebec

    -Return to Top-

    Hi Jay I did a posting http://www.hobby-machinist.com/thre...-to-a-tb6560-3-axis-driver-blue-boards.48391/

    and hope you can help me as it looks like you connected your VFD to Mack3 thanks
     
  28. jbolt

    jbolt United States Active User H-M Supporter-Premium

    Likes Received:
    844
    Trophy Points:
    113
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Hi dooshare,

    Welcome to the site. I'm not familiar with your board but it looks like it has built in spindle support. It there a manual for the board?

    I'm at work now but I can take a look later tonight to see if I can help but in the mean time you should post this in the" CNC in the Home Shop" forum so it will get better exposure to the CNCer's on the forum.
     
  29. dooshare

    dooshare Canada Iron Registered Member

    Likes Received:
    1
    Trophy Points:
    3
    City:
    sherbrooke
    State:
    Province du Quebec

    -Return to Top-

    Thanks Jay, i reposted it under CNC home shop with more info and photos.
     
  30. BillyT

    BillyT Canada Iron Registered Member

    Likes Received:
    1
    Trophy Points:
    3
    City:
    Clavet
    State:
    Saskatchewan

    -Return to Top-

    hey Jay, why does the max hertz have to be set to 125, should it not be 220....fyi i'm a fng
     