220v to 110v motor

bill stupak

Active Member
Registered
Joined
Feb 26, 2014
Messages
120
Can this motor be switched to 110v? It's from a Lienhard single lip cutter. I can, but would rather not run a dedicated 220v outlet for it.lienhard.jpglienhard 2.jpg
 

Asm109

Active Member
Registered
Joined
Aug 29, 2017
Messages
253
No. That is a 3 phase motor. You will need a converter or VFD to run on single phase.
 

benmychree

John York
H-M Supporter - Gold Member ($25)
Joined
Jun 7, 2013
Messages
3,855
It appears to be either 220 V or 440 V, and yes, 3 phase.
 

Superburban

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Jan 2, 2016
Messages
1,042
It appears to be either 220 V or 440 V, and yes, 3 phase.
I do not think so. usually multi voltage motors have 6 winding's to configure for the 2 voltages. I only see three, that can be swapped from y to delta configuration.
 

MikeInOr

Active Member
Registered
Joined
Jan 1, 2018
Messages
312
A 110v to 220v VFD would let you run that on 110v if it isn't too big of a motor. A 220v VFD would be better but if you have to run it on 110v then one of these would probably do the job. If the motor is more than 1hp you will probably need a 20amp 110v circuit for the vfd/motor.


https://www.amazon.com/KB-Electronics-KBMA-24D-Enclosure-Frequency/dp/B01AOCJT0K/ref=sr_1_5?keywords=120v+vfd&qid=1574548130&s=hi&sr=1-5


https://www.amazon.com/Huanyang-Variable-Frequenc-Controller-Inverter/dp/B07GD628D7/ref=sr_1_6?keywords=110v+to+220v+vfd&qid=1574548265&s=hi&sr=1-6
 
Last edited:

markba633csi

Platinum
Registered
Joined
Apr 30, 2015
Messages
4,324
Yes, it's 3 phase of unknown horsepower rating- 0.18 CH must be the size rating but not sure what units they are using. 3240 is the rpm. Hmm, Oerlikon, didn't they make firearms during the war?
Mark
 

bill stupak

Active Member
Registered
Joined
Feb 26, 2014
Messages
120
Other single lip cutters of this size are around 1/4 hp. I have found an alternate motor to use on it.
 