Not an electrician, but from what I have read "NEC to allow a 50A outlet on a 30A circuit if it's a single outlet circuit ( 210.21(B)(1) ). The only restriction is the outlet is not to have a amp rating less than the circuit. There is no restriction to the outlet being a higher rating than the circuit. But, on circuits with two or more outlets you need to use the values listed in table 210.21(B)(3) which would limit a 50A outlet to a 40A or 50A circuit." There may be also local codes in addition to the NEC. The key factor is a single dedicated socket as opposed to multiple.
The load must conform to the breaker size not the plug if rated higher than the breaker. There are also cases where the breaker is rated higher than the wire rated current such as VFDs and motors where their is a high surge and/or short term peak load. What I often will do is use an adapter plug to socket if say you have a 30 A socket and want to connect it to a 50A plug with a maximum 30A load.
Code? What is code? I guess living in the sticks has its' advantages.
Electricity only causes problems when it is flowing. If you are concerned about it, throw the breaker when you are done. If the wire can take 30 amps, and the breaker is 30 amps and you don't plan on drawing more than 30 amps, how it is connects to the circuit is a minor issue. I mean, as long as it isn't bare wires stuck into a potato, it will be good.If the shop were in a detached building I'd probably worry less, but it's right below our bedroom
Cheers,
John
If the capacitors are original replace them and that Millermatic 150 will weld better then most new ones. I have it's big brother
Electricity only causes problems when it is flowing. If you are concerned about it, throw the breaker when you are done. If the wire can take 30 amps, and the breaker is 30 amps and you don't plan on drawing more than 30 amps, how it is connects to the circuit is a minor issue. I mean, as long as it isn't bare wires stuck into a potato, it will be good.
But it is worth having breakers tested when you get to a certain point. As a past firefighter, I have seen a few fires started by breakers that failed to trip when the circuit was overloaded but exactly zero caused by having a circuit with a properly wired but overrated receptacle.
But then, I don't have an inspector looking over my shoulder. I'd be willing to bet 80% of the wiring in this town have never been inspected. You pay your money for a permit, or not and run the wires. Surprisingly, we don't really have that many fires that are electrical in nature.