As the title says I've finally saved up a few thousand to get my old bridgeport running! Some of you may remember me but for those that don't here's an overview of what's going on.
About a couple years ago I bought a 72 Bridgeport series 2 for a hell of a deal. It's been sitting in my shop collecting dust while I saved up for the day I could afford a phase converter and transformer! Well that day has come! And I'm looking for advice on how to go about setting this up and what size RPC and transformers I'd be looking at. (A VFD will not work as the mill has 2 other DC drive motors and I'd like to retain all factory features)
The mill has a 4HP 440 3 phase motor. I have 220 single phase. The plan is to go from 220 single to 220 3phase with an RPC then step that up to 440 3 phase with a transformer. I believe I would need a 10hp roto phase and a 15kva transformer. Anyone with experience in this kinda stuff please let me know if I'm atleast on the right path!?
 

markba633csi

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Apr 30, 2015
Messages
2,904
Likes
1,505
#2
What voltages do the dc drive motors use? Would there be any advantage to changing the spindle motor to a 220 volt unit? (cost, simplicity, etc.)
3 phase step up transformers are expensive, heavy to ship and incur losses
mark
 

Z2V

H-M Supporter - Sustaining Member
H-M Platinum Supporter ($50)
Joined
May 10, 2017
Messages
647
Likes
607
#3
Just curious and not being a Bridgeport owner myself, you said there are two DC motors also. I’m just wondering if there is a transformer before the DC power supply that is tapped for 220 and 440 volts? If so, is the 4 hp drive motor dual voltage? What I’m getting at is could you convert the machine to 220 volt and save the cost of a step up 3 phase transformer. I know some wiring would need to be changed to larger gauge to handle the higher current of the lower voltage. Like I said, I know nothing about your machine, just thinking through my finger tips.

Oh, I see @markba633csi beat me to the thought
 

Eddyde

Bronze
Registered
Joined
Oct 13, 2014
Messages
1,396
Likes
1,167
#4
I agree, see if the machine can be converted to 220v 3 phase.
Some pictures of the motor data plates, electrical cabinet, etc. will help.
 

Martin W

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Mar 26, 2014
Messages
372
Likes
331
#5
Izzy,
you probably do not need to go to a 10hp. 7-1/1 2 will do, but if you are running more than one machine bigger is better. Phase Quest is pretty reasonable for RPC,s. I run two, one 10hp and one 15hp for the last 15 years without much trouble other than a couple switches and bearings in one motor. The 15 hp runs 5 days a week. I also have a step up transformer from 240 volt to 600 volt . I bought it used about 10 years ago for cheap.
Cheers
Martin
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#6
Thanks for all the replies guys I appreciate all the feed back I hope nobody takes this the wrong way but, please stick to my questions. I've already done my fair share of research to know 220 single phase isn't an option in my situation.
@Martin W sounds like what I'm trying to accomplish is reasonable. I plan to build my own RPC that's the cheapest route. As far as transformers go how many KVA would I need? and would it be a bad thing to get bigger than I need? I see alot of 30kva units in my area for like 300 bucks... Just don't Wana buy something that won't work
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#7
For those that are wondering the entire control panel would have to be re-wired, motor starters, contactors, fuses would all need to be changed, transformers re-wired and finally the motor itself as it's permanently wound for 440. Not practical or economical at all vs just getting it running the way it's supposed to. I want to retain all factory features/fuctionality
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#8
Did I scare everyone away? :(
 

JimDawson

Global Moderator
Staff member
H-M Platinum Supporter ($50)
Joined
Feb 8, 2014
Messages
7,137
Likes
5,384
#9
Is this a CNC machine? A 30KVA transformer would be way overkill, but it would work fine.
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#10
See I figured 30kva would be alot more than I need but he's only asking 400 for it he'd probably let it go for 300 if I offered. The price is right i just want to make sure I won't let the smoke out of the ole girl before I get to use it!
Lol it's a 1972 Bridgeport series 2. No cnc.
So aside from it being big it would still run the machine?
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#12
Would I be consuming a rediculous amount of electricity cuz of its size or would it only output as much as the machine uses? I might just go ahead with this one it's a hell of a deal!
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#13
Sorry it was a 25kva. It's a step down but as far as I know I can back feed it? Here's the transformer in question. Will I have an issues back feeding it? ad_1535039145157.jpg
 

JimDawson

Global Moderator
Staff member
H-M Platinum Supporter ($50)
Joined
Feb 8, 2014
Messages
7,137
Likes
5,384
#14
There would be a small amount of power loss to heat, but it wouldn't be excessive. Transformers are pretty efficient, so don't worry about that.
 

JimDawson

Global Moderator
Staff member
H-M Platinum Supporter ($50)
Joined
Feb 8, 2014
Messages
7,137
Likes
5,384
#15
It will be happy going either direction.
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#16
Awesome! Thanks alot! Going to contact the seller now! :D
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#17
Someone was telling me the transformer may stall the rpc due to it's size? Is that a possibility? Id hate to buy something I can't use...
 

JimDawson

Global Moderator
Staff member
H-M Platinum Supporter ($50)
Joined
Feb 8, 2014
Messages
7,137
Likes
5,384
#18
Pretty sure it won't do that. It only takes an instant for the transformer to energize. Worst case put a switch between the RPC and the transformer. Start the RPC, then switch in the transformer.
 

Martin W

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Mar 26, 2014
Messages
372
Likes
331
#19
Hi Izzy
Did you pick up the transformer? The transformer I have is 15KVA. I have never noticed any heat from it or any difference in my Hydro bill.
I have a 2hp 440 volt motor that could not be rewound. My electric motor guy changed it from Delta to Wye or vice versa I am not sure. It has been running on 240 volts for about 6 years now with no issues. This doesn't help you with the contactors and fuses though.

Cheers
Martin
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#20
no i have not yet picked it up. im arranging a time for pickup currently. hopefully this will be my last question but i found a 5HP roto phase for sale for 300bucks would that whole setup work or is that roto phase to small? i would think i need 7.5-10hp but if not ill be set!
@Martin W its good to know i wont notice much on my hydro bill that was another of my worries :)
 

Cadillac STS

Active User
H-M Platinum Supporter ($50)
Joined
Jul 20, 2012
Messages
620
Likes
222
#21
When I first got my Bridgeport and powered it up it just blew the circuit breaker. Couldn’t figure it out for a while. Turns out the spindle brake was set on and the motor couldn’t turn. Turned off the brake and everything was fine!
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#22
I haven't gotten power to it to test out my breakers yet haha if y'all think I'll be ok with a 5hp roto phase I'll contact that guy and get my machine running!
 

Chipper5783

Active User
H-M Supporter - Gold Member ($25)
Joined
Sep 25, 2014
Messages
723
Likes
556
#23
If you want to go cheap, for the purpose of testing you do not need the transformer. You can run that 440V motor on 240V. Motor shops routinely run motors at reduced voltage when testing them (generally it is much higher voltage and larger motors than what you are considering, but the concept is the same). Of course you still need the RPC.

You can't run a low voltage motor from a higher voltage source (i.e. a 240V motor on 440V would not be good). There is no problem running a 440V motor at 240V - however, you must not exceed the motor nameplate full load current. That 4HP motor will be totally gutless (perhaps less than 50%), but you'll still have more capability than most mini-mills. Of course you still have to sort out the requirements for the table drives (which you said were DC) - but at least you will know that the main motor is good.

You will have a control transformer and it will have multi taps, so you'll need to move the tap connection so that your control power (which is single phase anyway) is the correct voltage for the coils. I always use the "real" power (which I set up on L1 & L2, with L3 being the generated leg) on the control transformer - not sure if that matters.

Your other question is whether that 5HP RPC is going to be adequate? That is a good question. I also have a 5HP RPC and I have two machines with 5HP motors: an air compressor and a lathe. The air compressor runs with no problem. The lathe has a 2 speed motor (3/5 HP) will trip the RPC if on the higher speed settings or with a heavy chuck or several starts close together. It has a manual speed switch - I don't change it on the fly.

I also have a 3 phase transformer 240-600V on my little milling machine (6kVA). It also has a 2 speed motor, which is 2.2 kW on the high speed (about 3HP), it struggles to start on high speed (sometimes it goes, sometimes it trips the RPC). This little mill has separate contactors for each speed so I hit the low speed button, then the high speed button.

If you are getting that 5HP RPC at a fair price - go for it and get your machine going. If it does not work out, you won't have trouble selling it on a fair price (may be a small loss).

Let us know how it works out. David
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#24
@Chipper5783 thanks! I'll contact the seller for the rpc! My only 3phase machine is my mill. The control panel transformers are already setup for 440 3phase so all I gotta do is hook up 440 3phase and it will all work. The transformers in the control panel feed the DC motors.
 

warrjon

Active Member
Registered
Joined
Jun 26, 2018
Messages
43
Likes
17
#25
Someone was telling me the transformer may stall the rpc due to it's size? Is that a possibility? Id hate to buy something I can't use...

You really only need 4KVa to easily run a 3kW motor as the mill does not start under load.

They are referring to inrush current and a 25KVa transformer this will be around 60 amps.

I would put the stepup transformer before the RPC and run the RPC at 440volts, this way the mains will be handling the inrush. Or add relay operated current limiting resistors that are switched out once the TX is on.
 
Last edited:

warrjon

Active Member
Registered
Joined
Jun 26, 2018
Messages
43
Likes
17
#26
You could run a VFD into the setup TX in place of the RPC and have over current control as the VFD will ramp the voltage up significantly lowering the TX inrush current. Don't know about the US but Down under my 4KW VFD was $200 and a RPC was $1500
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#27
im from canada. im getting both the transformer and phase converter for 400. its hell trying to find industrial type stuff in my area there was literally only one other RPC for sale in my entire province.... it was also a 5hp but was asking 600. its next to impossible to find a sinlge phase transformers at that high of a voltage normally anything over 220 here is 3 phase. i knew this thing would be alot bigger than i need but its literally the smallest 220/480 transformer i could find.... is it possible to have a shop lower the Kva rating?
 

warrjon

Active Member
Registered
Joined
Jun 26, 2018
Messages
43
Likes
17
#28
To give you an idea of how big a 25KVa TX is - I have a 10KVa TX on the pole outside my house feeding 3 houses from the HV. If I were you I find out just how big this 25KVa TX is, do you need a crane to move it.

Here is a pic of a 25KVa TX
https://www.indiamart.com/proddetail/25-kva-three-phase-transformer-13476189248.html

If you do go this way the 3 phase TX can still be put in the single phase, just use 1 phase of the TX.

If I were you I would seriously look at VFD's. My mill is 5hp with 110Vac power feeds running off a TX inside the mill cabinet. I have rewired my mill so everything runs and the original switches operate the mill. I do not use the coolant so this is disconnected. I have disconnected the main contactors as the VFD runs the motor directly.

Our single phase is 240V, I put a 240V power lead on the mill, changed the input tap (My TX was multi tap) from 415V to 220V. Then wired 240V directly out to the VFD, so the main power switch on the mill turns the VFD off.

I rewired the forward/reverse switch to the VFD so it controls F and R.

The motor was star only, so I had to find the star connection in the motor and bring it out to the terminal box, easy to do this took less than an hour including re-lashing the motor windings. If you are unable to do this any motor shop should do it for a reasonable cost.
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#29
i cant run a VFD because the motor is wired into a control panel in the back of the machine, power does not go directly to the motor. it goes through a set of contactors, fuses, and motor starters thats why i cant run a VFD. its not that i havent looked into it i thoroughly have when i first bought the machine the problem is this isnt your basic mill its a series 2 its a little more complicated. the panel needs to see 440 3phase and from my research a VFD is not a power source its a motor controller. correct me if im wrong but from what i can gather is the contactors wont work properly with power coming from the VFD the VFD has to power the motor directly correct? here is the transformer in question. add states 25kva. but i honestly dont have the slightest clue about that kinda **** tho it'd be like telling your wife the lawn mower has 500hp she'd believe it haha
 

Izzy

Active Member
Registered
Joined
Sep 22, 2016
Messages
351
Likes
150
#30
i had a motor shop look at the motor and its permnently wound for 440 volt and changing to 220 would require a new motor or a re-wind and that alone puts me well over the cost of a phase converter and rpc setup. then id stall have to buy all new fuses, contactors, and motor heaters so not only would that be exponentially more expensive it would also be alot more work. the conclusion ive drawn is the cheapest easiest possible route is the one im taking i just need a little help figuring out the details. heres the transformer in question, its the little guy. trans.JPG
 