One VFD for both lathe and mill

martik777

Active User
Registered
Joined
Apr 19, 2011
Messages
572
I never use both at the same time so why bother buying another VFD. What type of switch could I used to switch the 3 wires from the lathe to the mill?
 

markba633csi

Platinum
Registered
Joined
Apr 30, 2015
Messages
4,322
I know you've heard all the warnings about that but if you are going to do it, the switch just needs to be rated for the current, and you must not switch it when the vfd is on. also, you may need different settings in the unit for each motor
A three pole double throw drum switch is what you want, a hefty one
 

markba633csi

Platinum
Registered
Joined
Apr 30, 2015
Messages
4,322
Certainly the latter and possibly both if the unit can "sense" the absence of a proper impedance on the output
You want to have the vfd located between the two machines to mimimize the length of wiring to each motor.
I'm sure other members will chime in and tell you not to do it, so good luck if you do
(that switch you showed is only 2 pole I believe-- don't buy a switch without seeing the internal diagram)
 

Winegrower

H-M Supporter - Silver Member
H-M Supporter - Silver Member ($10)
Joined
Jul 29, 2014
Messages
454
The VFD has a bunch of configurable options for a particular motor. I think it would be fortuitous if your lathe and mill needed exactly the same settings. Perhaps it would not make enough difference to be a big issue, but you’d be on your own to figure that out.
 

martik777

Active User
Registered
Joined
Apr 19, 2011
Messages
572
Thanks, they are almost identical in HP with a base 60hz speed of ~700RPM which gives me a usable torque range of 200-1200RPM with 18-120hz

I don't use many settings, just fwd/rev and a max frequency threshold
 

Superburban

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Jan 2, 2016
Messages
1,041
I believe that switch is for fwd/off/rev, or high/off/low. You would want a switch with 9 terminals, 3 input, and 3 outputs for each motor.

Keep in mind, you do not want to use the factory on/off switches with a VFD, unless you have them wired to the VFD, to power the VFD. Trying to get all that wired up, and also be able to switch which motor they are using, will be a sanity check. Unless you are going to use the controls on the front of the VFD each time.

I seriously gave the same thing a lot of thought. I have a four head Fosdick drill press. Basically a humungus stand, and four individual identical drill presses. After a lot of thought, I went with 4 VFDs. It would not have been that hard, as all the motors are the same, and the controls at the front, But the switching, and possibility of the switches being turned, made the decision for me. Also, afraid of a accident by turning the VFD on, and it is niot switched to the drill press I am thinking it is.
 

markba633csi

Platinum
Registered
Joined
Apr 30, 2015
Messages
4,322
Looks like you want a switch with 12 terminals like one of these:
You would need to add 3 jumper wires, for example 2-3, 6-7, and 10-11 to create the 3 switching poles from the VFD, then motor A would connect to 1, 5, and 9 and motor B would connect to 4, 8, and 12
rotarysw12tblu.jpg
rotarysw12term.jpg
 

markba633csi

Platinum
Registered
Joined
Apr 30, 2015
Messages
4,322
I would get a switch rated at least 4 times the expected current, not necessarily for electrical reasons but because the switch will be better built internally with stronger parts less likely to melt or break apart and fry your VFD output stage
Import switches are notoriously weak and flimsy
 

Hawkeye

Active User
H-M Supporter - Gold Member ($25)
Joined
Jun 17, 2011
Messages
1,902
I used relays to switch between lathe and mill, including feeds for the MachTach. I added a relay connected to an output from the VFD so that the change could not be made unless the VFD output was at zero. Prevents the much-warned chance of burning out the VFD by having it powered with no load.

Cooter's suggestion will be the cheapest, but you have to make sure you never turn the VFD output on while the plug is disconnected. BTW, all the relays cost around $100. Could be done cheaper with PCB-mounted relays, though.
 

ch2co

Grumpy Old Man
H-M Supporter - Gold Member ($25)
Joined
Jan 9, 2013
Messages
988
Easier and more user friendly in the long run just to use two VFDs. IMHO
 

Cooter Brown

863 Bronze
H-M Supporter - Gold Member ($25)
Joined
Nov 23, 2017
Messages
778
I dont know where you are finding VFDs for $40, but I'd like to know.....

Dont ever but plugs at home depot they are way over priced....


 

martik777

Active User
Registered
Joined
Apr 19, 2011
Messages
572
I paid $56, they are 65 now and the same one is on for 29.99 but the seller is away (scam possible):


So far mine has worked perfectly

Thanks for the links
 

Winegrower

H-M Supporter - Silver Member
H-M Supporter - Silver Member ($10)
Joined
Jul 29, 2014
Messages
454
Just remember all the VFD manuals say no switches between the VFD and the motor? Think they just make that stuff up?
 

Cooter Brown

863 Bronze
H-M Supporter - Gold Member ($25)
Joined
Nov 23, 2017
Messages
778
Just remember all the VFD manuals say no switches between the VFD and the motor? Think they just make that stuff up?
I have a reversing switch wired to my VFD and then to the motor on my lathe, it works great.... Yes! That is a bunch of made up garbage.... lol
 

martik777

Active User
Registered
Joined
Apr 19, 2011
Messages
572
I wired my old drum switch the same way, also added an external pot for speed control. Don't trust those membrane switches to last long.vfd final.jpg
 

fixit

Active User
H-M Supporter - Gold Member ($25)
Joined
Feb 8, 2014
Messages
299
Wire a female plug to the VFD and then plug in the machine that you want to use.....
PERFECT NO FAIL way to do it & the price would be right also. With a little handy wiring, he could also have remote start/stop & speed control located at each machine. VFD's don't like start/stop, fwd/rev controls on output. All controls need to be in the VFD drive unit.
 

markba633csi

Platinum
Registered
Joined
Apr 30, 2015
Messages
4,322
Perfect except the cost of 3-prong twist lock plugs and receptacles is much more than a switch
 

Ben Nevis

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Mar 18, 2015
Messages
110
Even if you are able to come up with a satisfactory switching arrangement, it is not very likely that you will want the same parameters for both machines. A milling machine will typically have an end mill or drill bit mounted in the spindle, so ramping up to full speed in a second or two will be no problem, but if you have a three jaw chuck and a chunk of steel mounted in the lathe, (10-30 lbs) such a fast start or stop could be quite exciting, especially if it is a threaded spindle.
 

Cadillac STS

Active User
H-M Platinum Supporter ($50)
Joined
Jul 20, 2012
Messages
805
Some people think of a VFD as just a power supply to make 1 phase 220 from 3 phase 220 like a rotary phase converter. Just a power source, plug whatever in and it powers all. Rotary phase converter is like that.

But a VFD is specific to each motor it works with and parameters are set for the motor. (Or should be for best functioning). So could use same VFD with two similar motors but be careful with different motors. Could use same VFD and change the parameter set but that takes a little time, not bad if you do it repeatedly.
 

Superburban

H-M Supporter - Gold Member
H-M Supporter - Gold Member ($25)
Joined
Jan 2, 2016
Messages
1,041
I never use both at the same time so why bother buying another VFD. What type of switch could I used to switch the 3 wires from the lathe to the mill?
After giving this more thought. After its all said and done, you will likely spend over 1/2, if not over the full cost of a second VFD. Consider just buying 2 of the same VFD's. Makes all this mute, and tons easier to wire it all up. Plus, you have a second that can be switched between machines if one goes bad.
 

martik777

Active User
Registered
Joined
Apr 19, 2011
Messages
572
I agree, good to have a spare, never know how long those chinese VFD's will last.
 