I've got an older house, built in 1961, w 50A 2 phase power (2 hots, and a neutral) from the power pole.
For the past year or two, the APC UPS (battery backup power supply) has regularly been trigger, either from low or high voltage (drops down to below 90V or goes up to 140V or so), and sometimes will go back to 120V after a short time, and sometimes it'll just stay there until I turn something like a space heater on the other phase.
i finally got out a clamp-on ammeter to try to figure out what is going on.
i clamped it on each of the wires going into the house, got about 20A and 10A on the two live wires, but 0A on the neutral.
Inside the house at the main fuse box, there's the main fuse/shutoff, then all the smaller fuses below, with cables connecting the two areas.
for the two live wires, they are again 20A and 10A, but the neutral within the box is odd
neutral to power meter (power meter is between outside connection and fuse box) 3A
ground wire; 7A
neutral cable from smaller fuses to upper panel connection; 10A
these 3 wires are all screwed down together in one spot in the middle of the panel
Am I right in thinking that it shouldn't be working like this, in that somewhere between the fusebox and the power pole in the street, there is a broken connection on the neutral, and when fixed, it should carry roughly the difference between the 2 live wires and that almost no current should be going through the ground wire?
For the past year or two, the APC UPS (battery backup power supply) has regularly been trigger, either from low or high voltage (drops down to below 90V or goes up to 140V or so), and sometimes will go back to 120V after a short time, and sometimes it'll just stay there until I turn something like a space heater on the other phase.
i finally got out a clamp-on ammeter to try to figure out what is going on.
i clamped it on each of the wires going into the house, got about 20A and 10A on the two live wires, but 0A on the neutral.
Inside the house at the main fuse box, there's the main fuse/shutoff, then all the smaller fuses below, with cables connecting the two areas.
for the two live wires, they are again 20A and 10A, but the neutral within the box is odd
neutral to power meter (power meter is between outside connection and fuse box) 3A
ground wire; 7A
neutral cable from smaller fuses to upper panel connection; 10A
these 3 wires are all screwed down together in one spot in the middle of the panel
Am I right in thinking that it shouldn't be working like this, in that somewhere between the fusebox and the power pole in the street, there is a broken connection on the neutral, and when fixed, it should carry roughly the difference between the 2 live wires and that almost no current should be going through the ground wire?