Running a 220v AC/DC PSU from 3-Phase?

Jimustanguitar

Registered
Registered
Joined
Jan 28, 2018
Messages
10
Hey, all. I'm working on a vintage Van Norman mill that runs on 'low voltage' 3-Phase power. A buddy who does a lot of automation saved me a 3-phase contactor from the dumpster at work, and I'm planning how to wire it up. The contactor runs on 24VDC from a power supply that says it will take 100-240VAC at 50/60hz. When I measured the voltage across the legs of my 3-phase plug, I recall having 120ish and 220ish VAC depending on which phases I measured across... If the power supply is just a simple rectifier circuit, would it "care" that I was feeding it with two legs of 3-phase? Is there any reason that I couldn't just use the electric that I already have on the machine instead of having to run a second extension cord from the wall?

OI4jvXc.jpg
 
It will work fine on 2 of the 3 phase legs. But I don't understand why you would get 120 between 2 of the 3 phase legs. That is strange.
 
It will work fine on 2 of the 3 phase legs. But I don't understand why you would get 120 between 2 of the 3 phase legs. That is strange.
I think it was a measurement between two of the phases, not a single phase and ground... Maybe 220VAC 120deg off of another 220 has an average difference in the low 100's... It was a cheap multimeter, I'd check it more carefully before connecting it, to be sure.
 
Your 24 volt power supply is probably a switching type supply hence the wide input voltage range. No it won't care about the phases as long as the voltage is within the range.
Do you have 3-phase power there? Most homes don't by default.
Mark
 
Last edited:
Phase-to-phase voltages on 3-phase Y system should all be the same. If you are measuring "120-ish" voltages along with 220V then your 120V measurement is a 220 phase to neutral voltage-- that is 220 / 1.73= 127 V. You should have at least 4 wires plus a ground entering your receptacle. You need to establish which are the 3 phases, which is the neutral, and phase sequence. On the odd chance that you running Delta, then it is possible that your 120 V is a center tap on one phase - in which case you have no grounding conductor, and you will need to install a ground fault detector/trip circuit. With respect to control voltages, you can derive power to your transformer either from a phase to phase connection or from a phase to neutral connection -- depending on the rated primary voltage of the control transformer you are planning to use. Moreover, the contactor pic you posted appears to be a DC output contactor and not a 3-phase contactor.
 
Last edited:
Phase-to-phase voltages on 3-phase Y system should all be the same. If you are measuring "120-ish" voltages along with 220V then your 120V measurement is a 220 phase to neutral voltage-- that is 220 / 1.73= 127 V. You should have at least 4 wires plus a ground entering your receptacle. You need to establish which are the 3 phases, which is the neutral, and phase sequence. On the odd chance that you running Delta, then it is possible that your 120 V is a center tap on one phase - in which case you have no grounding conductor, and you will need to install a ground fault detector/trip circuit. With respect to control voltages, you can derive power to your transformer either from a phase to phase connection or from a phase to neutral connection -- depending on the rated primary voltage of the control transformer you are planning to use. Moreover, the contactor pic you posted appears to be a DC output contactor and not a 3-phase contactor.
BJJ, agree with most of your post but, to avoid confusion, the pic the OP put up is of his ac-24Vdc power supply not his contactor.
Cheers Tim

Sent from my SM-G950F using Tapatalk
 
BJJ, agree with most of your post but, to avoid confusion, the pic the OP put up is of his ac-24Vdc power supply not his contactor.
Cheers Tim

Sent from my SM-G950F using Tapatalk
Correct. The earlier picture was just the power supply. This is the contactor.
JUqKT1y.jpg
riqtPyY.jpg
 
BJJ, agree with most of your post but, to avoid confusion, the pic the OP put up is of his ac-24Vdc power supply not his contactor.
Cheers Tim

Sent from my SM-G950F using Tapatalk

My bad - thanks. Looking at it again, it clearly states "power supply"
 