One last thing to think about... On all my VFD, each requires that you specify (by programming the registers) the desired input voltage and incoming frequency. These things are designed to work in many counties where the input voltage could be 110, 220, 50Hz or 60Hz. You have to tell it what is being supplied. (With additional circuitry, they could determine that automatically but for cost saving, they make the user manually enter the values).
I'm swamped at the moment and can't look at the manual but, do look it over for those parameters... It's possible though that yours automatically senses input parameters.
If all this fails then, it's also possible (as others have noted) that your feed line is too long and is dropping voltage when load is applied. 12ga stranded wire would help that situation. When circuits start getting longer than about 75' (roughly) these types of problems can start to appear -especially when you're pulling more than 10-15 amps.
Ray
I'm swamped at the moment and can't look at the manual but, do look it over for those parameters... It's possible though that yours automatically senses input parameters.
If all this fails then, it's also possible (as others have noted) that your feed line is too long and is dropping voltage when load is applied. 12ga stranded wire would help that situation. When circuits start getting longer than about 75' (roughly) these types of problems can start to appear -especially when you're pulling more than 10-15 amps.