Hitachi WJ200 VFD - Access to all programming parameters via the keypad.
On power up, The keypad will light up and you will then be able to go into the PROGRAMMING mode. Use the program guides to determine how to make menu and keystroke settings for operating parameter changes if you are not using the ProDriveNext software. Before you can make "High Level" parameter changes and see the programming parameters "Full Display" you must first make the following to changes to the default parameter values:
1. Change B031 to "10". This unlocks all the high level program functions for editing.
2. Change B037 to "00" for full display of all functions. You must press both the up and down arrows to access single-digit edit mode since this feature is not accessible in the default basic display.
Without doing this first, the default WJ200 VFD settings limit access to changing many of the program parameters via the VFD keypad. This is the Security Lock Mode described in Section 3-53 of the manual and restriction of Display Related Parameters Section 3-57. These restrictions are not in place if you are programming through a computer with the ProDriveNext software, unfortunately the Hitachi software only runs on PC systems. So to run on a Mac you would needs some form of Windows emulation program. Since I use the software to set up the wj200 VFDs, I have not encountered this problem. But on one of my recent installation of a WJ200 for a plate roller system, this issue came up when the owner tried to make some parameter changes.