Hello everyone, first post. I built a rotary phase converter and all seems well except when the converter is started up the 10 hp motor shaft locks up I can’t turn it by hand until I turn off the converter. I tried moving the 3 phase wires around on the motor leads with no luck. I wired the motor for low voltage per the attached diagram. 73A0F858-B804-4407-8B97-D9CBBC8B5CCD.jpeg 1AE501F1-A6F3-451B-B061-2C0A15A10AEE.jpeg 27DFBCD8-A4E7-4399-8E84-EF68478F2A22.jpeg 50E982E0-4292-4CB8-9096-AB3C474CDBBA.jpeg
I have not been able to balance the voltage yet due to the motor not generating the 3rd leg. The motor is brand new out of the crate ( see photos) 60 amp breaker at supply panel.
Any help will be greatly appreciated.
 

markba633csi

H-M Supporter - Premium Member
H-M Supporter-Premium Member
Joined
Apr 30, 2015
Messages
2,362
Likes
1,226
#2
If it's humming loudly when it locks up then something must be mis-wired I would think- check your connections again- does the motor spin freely
when powered off? No problem with bearings? I'm also wondering if maybe you don't have enough starter cap?
Mark
 

dlane

Active User
H-M Supporter-Premium Member
Joined
Sep 27, 2014
Messages
2,870
Likes
1,310
#3
Alls not well if it locks up, sounds like the rpc motor to me. , Ied vfd it if doable
 

Esmith41

Swarf
Registered Member
Joined
May 29, 2018
Messages
7
Likes
3
2
#4
The start capacitor is around 500 micro ferands. Just to be clear this is the “pony” motor used to generate the three phase power that I am having trouble with. It spins freely when not energized. I will look at the motor wiring again.
 

Canus

Swarf
Registered Member
Joined
Mar 19, 2018
Messages
18
Likes
9
2
#5
Think your start capacitor is too small. Try a 750-850 mfd 400 volt. Usually a good rule of thumb is 75+ mfd per horsepower.
 

JimDawson

Global Moderator
Staff member
Active Member
Joined
Feb 8, 2014
Messages
6,681
Likes
4,845
#6
I'm having a little trouble following your wiring in the panel, could you provide a drawing of the circuit?
 

Esmith41

Swarf
Registered Member
Joined
May 29, 2018
Messages
7
Likes
3
2
#7
Here you go. I am by no means an electrician or electrical engineer but here are “my schematics”. Probably not much better than the picture of the RPC. 90D89C36-195B-4B77-8499-6C680127D1BD.jpeg
 

markba633csi

H-M Supporter - Premium Member
H-M Supporter-Premium Member
Joined
Apr 30, 2015
Messages
2,362
Likes
1,226
#8
I'm not 100% sure but I think your pushbutton might be miswired-
 

JimDawson

Global Moderator
Staff member
Active Member
Joined
Feb 8, 2014
Messages
6,681
Likes
4,845
#9
The attached PDF might help you. As @markba633csi said, I think the double throw switch is wired incorrectly. In the attached file, you can ignore the control power transformer and use full voltage coils in the contactors. The main idea is to temporarily connect the start cap between one of the input legs and the manufactured leg. Cpf in the drawing is not required, but does make the system more efficient.
 

Attachments

Esmith41

Swarf
Registered Member
Joined
May 29, 2018
Messages
7
Likes
3
2
#10
I highlighted the circuit for the start capacitor. I think I have it wired correctly. The only thing I see I could do differently is move the the supply power for the capacitor from the load side of the contactor to the line side. This would give power to the capacitor before switch is pushed and the contactor is pulled in. I have of the the momentary switch throws filed down so the capacitor is energized a split second after the contactor is energized.
Thanks for your suggestions everyone, Just talking about it and getting a different set of eyes on it make me think a little different and hopefully gets me closer to a solution.
Eric
 

Attachments

markba633csi

H-M Supporter - Premium Member
H-M Supporter-Premium Member
Joined
Apr 30, 2015
Messages
2,362
Likes
1,226
#11
Your switch symbol is not clear, it looks like the contacts connect top to bottom? Tip: use standard schematic symbols
A la:
2psw1a.jpeg Mark
 

JimDawson

Global Moderator
Staff member
Active Member
Joined
Feb 8, 2014
Messages
6,681
Likes
4,845
#13
After looking at your drawing, I think I agree that it's wired correctly. If your switch is wired correctly it looks like it should start the motor when the switch connects the start cap to the circuit. I think the start cap needs to connect before the contactor closes, then disconnect when the motor is spun up.
 

Esmith41

Swarf
Registered Member
Joined
May 29, 2018
Messages
7
Likes
3
2
#14
I found a loose spade end on one of the connections at the start capacitor. I repaired the end and the motor spun instead of locking up. It would not get up to speed so I’m thinking it will need another 300 mfd start capacitor to get it up to speed on the start. It may be awhile before I can get to it but I will let you know how it turns out.
Thanks again for your help.