The motor must be designed to run at 2 speeds. Most are not 2 speed. Info on the motor-plate will tell you. I assume your service power is single phase 220. If your switch-box was made for 3 phase, it's unlikely it can be reused for single phase.
Sounds like you're converting a 3-phase machine to single phase. You might consider keeping the 3-Phase motor and using a VFD to convert single phase to 3-phase. If you go that route, you should not put a switch in between the VFD and motor as it will burn-up the VFD in time.
Tell us more about what you're up to and maybe there's a solution.
Also, if you're not familiar with motor wiring, try to find someone with knowledge to watch over your shoulder. -Might spare you from burning-up a motor or shocking yourself.