Thanks Bi11Hudson - just so I am correctly understanding your guidance here, you are saying to wire the conductors from the subpanel to the VFD at the input rating of the VFD (10A) plus 20% (so 12A). I am interpreting the second part of the guidance to mean the conductors from the VFD to the motor, which would be the rating of the machine load (motor) x 1.73 + wiggle room. I am not sure if I am interpreting this correctly or not.
Thanks
Tom
What I was trying to convey is that the 3 phase load (VFD to motor) will be as the load (motor) is rated. From the source to the VFD (single phase) will be 1.73 times the name plate rating of the motor. On top of that, add a little wiggle room, both from the source to VFD and from the VFD to the motor.
In both cases, the NEC requires circuits to be loaded with a
normal maximum of 80% of the breaker rating. That's where the 20% wiggle room came from. You already have that where your VFD is rated larger than your motor. I'm more concerned about from the source to the VFD. When you convert the single phase to 3 phase, the power has to come from somewhere. The 1.73, square root of 3, is the accepted factor for calculating single phase to three phase conversion.
It is just my opinion, but from the sounds of it your solar conversion was done by a wireman, not an electrician. The state doesn't draw a distinction between the two. Both can get a license. I have never had a license as such, but in industrial work as an inhouse electrician, a wireman doesn't last very long. And sometimes gets somebody killed. . .
You can clean up your panel yourself, if you're not nervous about it. Once you turn off the breakers, it's just a piece of wire. But if it's fed from the solar as well, it's still hot with one breaker off. Other than that, you kill the breakers, cut the wire shorter, and put it back where it came from, dressing the wire as you go. Electricity isn't dangerous as long as you know what not to do. If you don't know that, your electrician will. And can do the job for you.
Putting larger wires into your panel is something that any residential wireman can handle. And likely does on a regular basis. You might want to 'up the ante' a bit though, as it
is more work. But if you expand, be sure to do it right so it can be expanded again later. The individual details would mean very little to you, but your electrician already knows them. Or should. . .
When I bought my house, it needed to be rewired. Built in 1887 or so, it had 120 volts 30 amps service from around 1920. I put in a 250 amp 240 volt panel, a Sq. D type QO 42 slot panel. And filled it. . . After 45 plus years, I have 3 outbuildings and 2 panels of 100 amps each. Fed off of one 75 amp submain. Only one because I can only be at one or the other at any given time. And never run a machine unattended. My generator is only good for 30 amps at 240 volts. And my solar is completely independant of the incoming line.
.