Easier to grab a big handle on a disconnect in an emergency that fumbling for a breaker tab.
In that case you really want a contactor so that you can kill power by hitting a button.
Easier to grab a big handle on a disconnect in an emergency that fumbling for a breaker tab.
I'd like to add a disconnect for the entire 220v service in the garage, so I can switch everything off when I'm not working. I have a 30amp fused safety switch which I was planning to use.
The purpose of any fuse/breaker is to protect the WIRE between the load center and the load. Assuming that your 240V receptacle is the only load on that circuit, a fuse/breaker on that circuit in the garage is redundant because the fuse/breaker at the main load center is protecting the wire.
First, if the switch is fused, you should be able to swap in smaller rated fuses. I would use a slow blow 20A fuse.
Second, while the "code lawyers" will probably say otherwise, I would go ahead and use it, even with the 30A fuse. It will work fine as a disconnect. If you do overload the circuit the fuse/breaker in the main load center will trip and you will have to walk to that location to reset it.
Hmm 120 amp is essential.Yes we should use at least at most 120 amp. It will never be harmful for your welder circut. It will make your machine circuit never stop.