There is no EMI/RFI filtering on the Teco VFD unless you add one. There is extensive information as too the leakage issue with VFDs, some manufactures have taken extensive and costly measures to minimize this and electrical noise radiation, but not at this level. The design of the line filter has an effect on the GFCI trip characteristics, the ones I typically use for electrical noise attenuation will outright trip them because of a high (intentional) leakage current to ground. I have used the TDK/LAMBDA-MC1230 noise filters on some VFD systems, they are rated at less than 1 mA of leakage current. Worth a try, connect it close to the VFD.
https://www.ebay.com/itm/LAMBDA-MC1230-Surplus-New-In-factory-packaging/391809295708
Sometimes there can be slight variations between GFCI's as to tripping, but they all most meet the same trip criteria for a Class A ground fault. I have worked with a number of individuals who have used the same Teco and all had the same issue with the GFCI tripping (these were the 120V version). There may be some variations from VFD model to model brand to brand, but this is a "known" problem with VFDs with no quick or "cheap" fix other than to wire a socket without a GFCI. You will have one GFCI feeding a branch of downstream sockets, you can move the GFCI to the next socket down and use the first as a non-GFCI and if you need to meet code, hard wire it. QED.
ABB Reference document. These have already been stated.
LINE SUPPLY GFCI CIRCUIT BREAKER’S AND AC DRIVES
Description:
Can a GFCI circuit breaker be installed on the AC power feeding a drive, or will the drive cause it to trip?
Answer:
The AC Drive most likely will cause the GFCI protection device to trip. The reason the AC Drive will cause this tripping of the GFCI is the Common Mode Current or Common Mode Noise (CM Noise) that the VFD is producing. The high rate that the IGBT is switched on and off is around (1 - 16 kHz). This switching creates Common Mode Electrical Noise. The Common Mode Noise is the current that appears on a conductor with respect to ground. This Common Mode Noise can and will travel throughout the plants ground system and even beyond. This Common Mode Noise can affect the operation of the application, and other equipment in the plant by interfering with signals from sensors, computers, PLC’s, telephone and radio. The VFD does provide ground fault protection on the output of the VFD.
Documents or other reference material: None
Corrective Actions:
The goal is to have all the Common Mode Noise return to the VFD. Here are some actions that will help reduce or eliminate the tripping of the GFCI. The motor cable should be VFD rated motor cable and the motor and shield should be grounded back to the VFD. The User Manual will provide information on how to correctly install the VFD. The installation of RFI/EMC filters before or inside the VFD. Installing an isolation transformer before the VFD and after the GFCI circuit breaker will help reduce the tripping of the GFCI.
https://www.ebay.com/itm/LAMBDA-MC1230-Surplus-New-In-factory-packaging/391809295708
Sometimes there can be slight variations between GFCI's as to tripping, but they all most meet the same trip criteria for a Class A ground fault. I have worked with a number of individuals who have used the same Teco and all had the same issue with the GFCI tripping (these were the 120V version). There may be some variations from VFD model to model brand to brand, but this is a "known" problem with VFDs with no quick or "cheap" fix other than to wire a socket without a GFCI. You will have one GFCI feeding a branch of downstream sockets, you can move the GFCI to the next socket down and use the first as a non-GFCI and if you need to meet code, hard wire it. QED.
ABB Reference document. These have already been stated.
LINE SUPPLY GFCI CIRCUIT BREAKER’S AND AC DRIVES
Description:
Can a GFCI circuit breaker be installed on the AC power feeding a drive, or will the drive cause it to trip?
Answer:
The AC Drive most likely will cause the GFCI protection device to trip. The reason the AC Drive will cause this tripping of the GFCI is the Common Mode Current or Common Mode Noise (CM Noise) that the VFD is producing. The high rate that the IGBT is switched on and off is around (1 - 16 kHz). This switching creates Common Mode Electrical Noise. The Common Mode Noise is the current that appears on a conductor with respect to ground. This Common Mode Noise can and will travel throughout the plants ground system and even beyond. This Common Mode Noise can affect the operation of the application, and other equipment in the plant by interfering with signals from sensors, computers, PLC’s, telephone and radio. The VFD does provide ground fault protection on the output of the VFD.
Documents or other reference material: None
Corrective Actions:
The goal is to have all the Common Mode Noise return to the VFD. Here are some actions that will help reduce or eliminate the tripping of the GFCI. The motor cable should be VFD rated motor cable and the motor and shield should be grounded back to the VFD. The User Manual will provide information on how to correctly install the VFD. The installation of RFI/EMC filters before or inside the VFD. Installing an isolation transformer before the VFD and after the GFCI circuit breaker will help reduce the tripping of the GFCI.