[4]
GS1 VFD programming
[3]
[10] Like what you see?
Karl_T
H-M Platinum Supporter ($50)
Oct 14, 2014
1,174
I bought this VFD from automation direct
https://www.automationdirect.com/adc/Shopping/Catalog/Drives/GS1_(120_-z-_230_VAC_V-z-Hz_Control)/GS1_Drive_Units_(120_-z-_230_VAC)/GS1-10P2
I want to use it to run a fan. When power is applied, fan runs. That's it. Pot on VFD will set speed.
With below settings, the fan will not start with a jumper between CM and D11. If the VFD is powered up, then CM and D11 is jumpered later the fan runs. In other words it needs a delay on to work correctly. (Manual states CM to D11 will cause run forward with correct params)
OK, I set the params to remote control. Tried both 3-00 set to 1 and 2
tried both 3-01 set to 0 and 1.
There must be a way to program this unit to just run when power is applied.
Suggestions?
mksj
Jun 12, 2014
2,168
Try the following if you want the VFD to go into directly to a run mode on power up with a jumper from COM to input DI1:
P6.02 Momentary Power Loss = 01: Continue operation after momentary power loss, speed search from Speed Reference
P6.30 Line Start Lockout = 01: Disable Line Start Lockout
Also P2.00 should be set to 2 for the torque setting for fans and pumps, along with the motor parameters.
Automation Direct has very good tech support, so if the above does not work I would give them a call.
westerner
If you are gonna be stupid, ya gotta be TOUGH!
Mar 29, 2017
261
+1, you bet
I bought a GS ll. The manual was written by some one who's FIRST language was English, their catalog is full of great info, the shipping was just as they said, etc., etc., etc. I am looking at another piece of machinery that would require a VFD, and there is no doubt where it would come from. In fact, my experience with Automation Direct has completely removed any trepidation I have ever felt about three-phase equipment.
I ain't shillin', I am just a hardheaded redneck trying to make some parts that fit, on a redneck budget.
Karl_T
Oct 14, 2014
1,174
Try the following if you want the VFD to go into directly to a run mode on power up ...
BINGO you da man!
I am guilty of not reading the big manual. Spent an hour with it last night. WOW, there is a ton of functionality on these drives I never knew about. And all for under $100.
And YES, I only buy from Automation Direct. You might find a smidgen lower price but you won't find better service and support on their top quality products.
[5] [7]