The transformer in the picture is not 3 phase. It can be used with 3 phase power, but it's not fed with all 3 phases.
The reason it's labeled with 220 and 480 is that 220 or 480 3 phase is the voltage developed between any two phases of the line.
As a side note, if you measure actual 3 phase to ground / neutral you get 277 for 480 and 120 if it's 208/220.
To feed the transformer you are going to hook 2 phases to it. One will connect to H1 with a jumper over to H3 and the other phase will connect to H2 with a jumper to H4. X1 and X2 are the 110 volt AC output that will run to the control circuits for the DC motor.
On a side note, if you were to feed the transformer with 480. The two phases would connect to H1 and H4 and a jumper would be placed between H2 and H3 for correct wiring.