Mike, here's something that I looked at this evening...
C and A in the RPC panel are the incoming single phase lines and B is the "wild leg". Inside the idler motor, I had the "wild leg" hooked up to L2, so to speak. I have since changed that to L3. Then, where the 3-phase power comes out of the RPC to a female plug, I made sure that the "wild leg" goes to L3 in the mill panel terminal.
Before I did this, the "wild leg" went to L2 in the idler motor. Would this have had any affect on the issue ?
Brian
anytime you change 2 of the 3 hot wires or the 2 supply wires place in relation to each other, you will reverse the rotation of the RPC and any motor hooked up to the RPC.