Central machinery 12x36 lathe wiring

Getting closer, a few things to tidy up, should be able to finish it Sunday night, thanks for the help
 

Attachments

  • IMG_4496.jpeg
    IMG_4496.jpeg
    522.1 KB · Views: 33
  • IMG_4495.jpeg
    IMG_4495.jpeg
    510.6 KB · Views: 34
Finally got to finishing it up, here are a few pictures, I really appreciate the help, just need to tidy a few things up
 

Attachments

  • IMG_4519.jpeg
    IMG_4519.jpeg
    501.1 KB · Views: 33
  • IMG_4518.jpeg
    IMG_4518.jpeg
    563.4 KB · Views: 35
  • IMG_4517.jpeg
    IMG_4517.jpeg
    541.7 KB · Views: 37
I think I see one mistake- right contactor, top row, metal jumper between 1 and R/L1- should not be one there
 
Your right, got it taken care off
 

Attachments

  • IMG_4523.jpeg
    IMG_4523.jpeg
    526.5 KB · Views: 34
I think it might be ready to test- try it first without the motor and see if anything blows
You should hear one each contactor clack for F and R
If that checks then hook up motor:
U & V to 1 & 4
M5 to 8
 
Last edited:
Just tried it, nothing sounds like it is making contact, wired motor and it doesn’t spin, I’m going to triple check everything and see what I have
 
Last edited:
OK- I'll take a look also. No contactor action means no power to coils- I would check for 120v power at the transformer
output lower terminals

I don't see anything- maybe a bad crimp connection?
 
Last edited:
I have 48.3 volts on x1 of transformer and 8.5 on x3 of transformer
 
You need to measure between x1 to x3 with meter on ac volts
I suspect fuse might have blown
 
Last edited: